AC Current Transducer APR-B10
Split-core transducer for the electronic measurement AC current (all
waveforms), with galvanic separation between the primary circuit and
the secondary circuit. Switch selectable measuring ranges and true
rms 0-5 V and 0-10 V switch selectable voltage output.e
PN
= 10 ... 400 A
Elecrical data
Primary nominal current
PN
(At.rms)
10, 25, 50
50, 75, 100
100, 150, 200
200, 300, 400
U
SL
SL
Î
Output voltage (Analog)
OUT
(V DC)
0-5 or 0-10
0-5 or 0-10
0-5 or 0-10
0-5 or 0-10
Types
APR 50 B10
APR 100 B10
APR 200 B10
APR 400 B10
+24 ±5 %
≥ 10
< 30
no limitation
RoHS since
date code
46184
46304
46194
47150
V DC
kΩ
● VFD and SCR waveforms current
measurement
● True rms output (average)
● Split-core type
● 0-5 V DC and 0-10 V DC switch
● DIN rail or Panel mounting
● Switch selectable measuring
ranges
● Insulating plastic case recognized
according to UL 94-V0.
Supply voltage
Load resistance
Output voltage limitation (0-10 V)
Output voltage limitation (0-5 V)
Maximum current consumption
Overload capability
Advantages
● Large aperture for cable up to
18 mm
● High insulation between primary
and secondary circuits
● Eliminates insertion loss
● Easy installation.
Accuracy - Dynamic performance data
ε
OE
TCV
OE
TCV
OUT
r
BW
Accuracy @
PN
= 25 °C (excluding offset)
Linearity error (0 … ±
PN
Electrical offset voltage @
= 25 °C
Temperature coefficient of
OE
OUT
(% of reading)
Step response time to 90 % of
PN
Frequency bandwidth (±1 %)
< ±1
< ±0.5
< ±0.5
±1
±0.1
< 400
30 … 6000
% of
PN
% of
PN
% of
PN
mV/K
%/K
ms
Hz
VFD Controlled Loads:
VFD output indicates how the
motor and attached load are
operating.
SCR Controlled Loads:
Accurate measurement of phase
angle fired or burst fired (time
proportioned)
SCRs. Current measurement
gives faster response than
temperature measurement.
Switching Power Supplies and
Electronic Ballasts:
True rms sensing is the most
accurate way to measure power
supply or ballast input power.
General data
m
IPxx
Ambient operating temperature
Ambient storage temperature
Mass
Protection degree
−20 … +60
−20 … +85
90
IP 20
g
Application domains
● Energies and Automation.
N°74.45.25.200.0; N°74.45.34.200.0; N°74.45.44.200.0; N°74.45.48.200.0
11May2015/version 6
LEM reserves the right to carry out modifications on its transducers, in order to improve them, without prior notice
Page 1/4
www.lem.com
Insulation coordination
U
b
Rated insulation rms voltage
1)
with IEC 61010-1 standards and following conditions:
- Reinforced insulation
- Over voltage category CAT III
- Pollution degree PD2
- Heterogeneous field
Rms voltage for AC insulation test
2),
50 Hz, 1 min
Partial discharge extinction rms voltage @ 10 pC
Impulse withstand voltage 1.2/50 µs
Creepage distance
Clearance
Comparative tracking index (Group I)
1)
U
d
U
e
Û
d
CP
d
CI
CTI
Notes:
5.5
5.5
kV
kV
kV
mm
mm
If insulated cable is used for the primary circuit, the voltage category
could be improved according to the insulation coordination given by the
cable manufacturer.
For example:
Cable insulation (primary)
Category
HAR 05
600 V CAT III
HAR 07
1000 V CAT III
Between primary (completely filling the primary aperture) and secondary.
2)
Page 2/4
11May2015/version 6
www.lem.com
Safety and warning notes
In order to guarantee safe operation of the transducer and to be able to make
proper use of all features and functions, please read these instructions thoroughly!
Safe operation can only be guaranteed if the transducer is used for the purpose it
has been designed for and within the limits of the technical specifications.
Ensure you get up-to-date technical information that can be found in the latest
associated datasheet under www.lem.com.
Caution! Risk of danger
Ignoring the warnings can lead to serious injury and/or cause damage!
The electric measuring transducer may only be installed and put into
operation by qualified personnel that have received an appropriate
training.
The corresponding national regulations shall be observed during
installation and operation of the transducer and any electrical conductor.
The transducer shall be used in electric/electronic equipment with respect
to applicable standards and safety requirements and in accordance with all
the related systems and components manufacturer’ operating instructions.
Caution, Risk of electrical shock
When operating the transducer, certain parts of the module may carry
hazardous live voltage (eg. primary conductor, power supply).
The user shall ensure to take all measures necessary to protect against
electical shock. The transducer is a build-in device containing conducting
parts that shall not be accessible after installation.
A protective enclosure or additional insulation barrier may be necessary.
The transducer shall not be put into operation if the jaw opening is open
(split core version) or the installation is not completed.
Installation and maintenance shall be done with the main power supply
disconnected except if there are no hazardous live parts in or in close
proximity to the system and if the applicable national regulations are fully
observed.
Safe and trouble-free operation of this transducer can only be guaranteed if transport,
storage and installation are carried out correctly and operation and maintenance are
carried out with care.
Page 3/4
11May2015/version 6
www.lem.com
Dimensions AP(R)-B10
(in mm)
(unit : mm, 1mm = 0.0394 inch)
Output Vo ltage
Selection Switch
Front Vie w
55
Rang e Selection Switch
14.80
4.7 0
Left View
16.40
40(distance between screws)
33.50
37
Axis of ape rture
67
21
Plug-in connector included : XW4B-03C1-H1 (OMRON)
18.50
Bottom View
0-5, 10V Selectable
0-5, 10V Selectable
OUTPUT
OUTPUT
AP/APR
+24VDC
+24VDC
Connections
Connections
Connections
AP/APR
Output
Connector Output
3(-) 2(out)1(+)
Connector
3(-) 2(out)1(+)
Output Switch
Range Switch
Front
Output Switch
Range Switch
Front
up to
⌀ 2
Wires
Wires up to
mm
mm
connectorto
2 mm
Female
up provided (spring terminal blocks)
Female Wires
connector provided (spring terminal blocks)
Female connector provided (spring terminal
direct
User-friendly spring-cage connection for no-tool
User-friendly spring-cage connection for no-tool direct blocks)
conductor connection
User-friendly
conductor connectionspring-cage connection for no-tool direct
Mechanical characteristics
● General tolerance
±1 mm
Primary aperture
18.5 mm
+24VDC
Ip
For panel mounting, replace M4 screws
+24VDC
supplied) with appropriate length to panel
OUT
● Panel mounting
2 holes
4 mm
General tolerance
aperture
Distance between holes
40 mm
± 1 mm
Primary General tolerance
For panel mounting, replace M4 screws by new
18.5
(not
Primary
one
mm
Panel
mounting aperture
supplied) with appropriate length to panel’s thickness.
Panel mounting
2 holes
4.0 mm
Distance between M4 screws by new one (not mm
40.0
For panel mounting, replaceholes
by new one (not
supplied) with appropriate length to panel´s thickness.
OUT
Is
DIN size35.50
69
Page 4/4
11May2015/version 6
www.lem.com
Page 4/4
080212/5
LEM reserves the right to carry out modifications on its transducers, in order to improve them, without prior notice.
www.lem.com